Hello, we have a program running on a CR1000 that is taking data from a LI-COR 7200 on a profile system of 14 levels for gas and temperature. I know that one gas sampling level has a faulty tubing, so that the data is no use. What is the best approach to label that data in the output table as NAN?I tried an If / Then statement in the scan operation but this doesn't work. I also tried a similar If statement in the CallTable command, but this didn't seem to work.
I suppose the best option is to put an If statement in the scan with limits for CO2 and H2O output, so that beyond or below a certain value it writes NAN.
Anyone have a suggestion, Thanks, Paul
The program is below
'Se-Sva_Profile_007; Lines 424-426 and 442-444 added If Then statement to put IRGA gas values to NAN when on Level 5 'Psmith 2022-11-11 'SE-Sva_Profile_004; Changed parameter agc to Signal_Strength for new firmware in 'Licor 7200 131009/ In Situ VE 'SE-Sva_Profile_003; 200ms scan for Li, 250us integration for all TC and Pt100 meas. 'Lapses parameter in DataInterval declarations set to 0 to force the logger to time stamp 'all records 'SE-Sva_Profile_002 changed default settings for seqencestep to 30s and Skip_s to 25s 130510/VE 'SE-Sva_Profile_001 'CR1000 Series Datalogger 'program author: Bengt Noren ,In Situ, 20130120 'Declare Public Variables Public PTemp Units PTemp=C Public batt_volt Units batt_volt=V Public ToRestart 'LI-7200 Public irga_fast(10) Public irga(10) '1s irga data (avg of irga_fast) Alias irga(1) = CO2_dry Alias irga(2) = H2O_dry Alias irga(3) = CO2_dens Alias irga(4) = H2O_dens Alias irga(5) = Signal_Strength 'Alias irga(5) = agc Alias irga(6) = P_fast Alias irga(7) = T_in Alias irga(8) = T_out Alias irga(9) = Tavg_Tin_Tout Alias irga(10) = Aux1 Units CO2_dry = umol/mol Units H2O_dry = mmol/mol Units CO2_dens = mmol/m3 Units H2O_dens = mmol/m3 Units Signal_Strength = arb 'Units agc = arb Units P_fast = kPa Units T_in = C Units T_out = C Units Tavg_Tin_Tout = C Units Aux1 = mV Public CO2_wet_ETC_fast Public H2O_wet_ETC_fast Public CO2_wet_ETC Units CO2_wet_ETC=umol/mol Public H2O_wet_ETC Units H2O_wet_ETC=mmol/mol Dim T_cell_ETC Dim PRESS_cell_ETC Units T_cell_ETC=C Units PRESS_cell_ETC=kPa Dim Level_ETC Public Flow_meter_raw_ETC Units Flow_meter_raw_ETC=mV Public Flow_meter_ETC Units Flow_meter_ETC=L/min Dim NAN_to_full_30min 'Control of two SDMCD16 'used to control magnetic valves and pumps 'M(m,n) = 1 / 0 for 0n / off 'M(m,n)=2 for auto control via logger program algorithms Public M(2,16) 'On / off / auto select. Normally left in auto mode, but can be 'set by opeator to on or off for system test Public a(2,16) 'from program logic, used in auto mode! Public o(2,16) 'actual state 'DO channel assignment for the two SDMCD16 Alias M(1,1) = M_Level_1 Alias M(1,2) = M_Level_2 Alias M(1,3) = M_Level_3 Alias M(1,4) = M_Level_4 Alias M(1,5) = M_Level_5 Alias M(1,6) = M_Level_6 Alias M(1,7) = M_Level_7 Alias M(1,8) = M_Level_8 Alias M(1,9) = M_Level_9 Alias M(1,10) = M_Level_10 Alias M(1,11) = M_Level_11 Alias M(1,12) = M_Level_12 Alias M(1,13) = M_Level_13 Alias M(1,14) = M_Level_14 Alias a(1,1) = a_Level_1 Alias a(1,2) = a_Level_2 Alias a(1,3) = a_Level_3 Alias a(1,4) = a_Level_4 Alias a(1,5) = a_Level_5 Alias a(1,6) = a_Level_6 Alias a(1,7) = a_Level_7 Alias a(1,8) = a_Level_8 Alias a(1,9) = a_Level_9 Alias a(1,10) = a_Level_10 Alias a(1,11) = a_Level_11 Alias a(1,12) = a_Level_12 Alias a(1,13) = a_Level_13 Alias a(1,14) = a_Level_14 Alias o(1,1) = o_Level_1 Alias o(1,2) = o_Level_2 Alias o(1,3) = o_Level_3 Alias o(1,4) = o_Level_4 Alias o(1,5) = o_Level_5 Alias o(1,6) = o_Level_6 Alias o(1,7) = o_Level_7 Alias o(1,8) = o_Level_8 Alias o(1,9) = o_Level_9 Alias o(1,10) = o_Level_10 Alias o(1,11) = o_Level_11 Alias o(1,12) = o_Level_12 Alias o(1,13) = o_Level_13 Alias o(1,14) = o_Level_14 Alias M(2,1) = M_Cal_1 Alias M(2,2) = M_Cal_2 Alias M(2,3) = M_Cal_3 Alias M(2,4) = M_Cal_4 Alias M(2,15) =M_VentPump Alias M(2,16) =M_SmplPump Alias a(2,1) = a_Cal_1 Alias a(2,2) = a_Cal_2 Alias a(2,3) = a_Cal_3 Alias a(2,4) = a_Cal_4 Alias a(2,15) =a_VentPump Alias a(2,16) =a_SmplPump Alias o(2,1) = o_Cal_1 Alias o(2,2) = o_Cal_2 Alias o(2,3) = o_Cal_3 Alias o(2,4) = o_Cal_4 Alias o(2,15) =o_VentPump Alias o(2,16) =o_SmplPump 'MAGNETIC VALVE SEQUENCING AND GAS MEAS. CONTROL Public Level 'Current sample level Public LevelSequence(33)'default sequence for Svartberget; 1,2,3...15. 'Normally 15 step is enough. 33 steps also accomodates for a up/down sequence; '1-2-3...15 and then 15-14-13-...1 'so all 33 do not need to be used. The first "0" in the table is interpreted by 'program logic as "end of sequence", and the sequence will restart from level in 'LevelSequence(1) Public LevelIndex 'Pointer to current selection in LevelSequence() Public SequenceStep As Long '_s 'second per level in sequence Public Skip_s As Long 'no of seconds to skip before averaging gas measurement, 'after switching to new level Public Store_Trig As Boolean'variable evaluated from user entered info on 'SequenceStep_s, triggers the averaging of collected data for one level before the 'next level is activated, 'A record is generated if Store_Trig is true Public Skip As Boolean 'varable evaluated from user entered info on SequenceStep and 'Skip_s. If true, the current sample is skipped! Public RUNAUTOSEQ As Boolean 'If true the auto sequence defined by the settings above will be run! Public n 'iteration counter for program loops. Public RS_R0 'intermediate storage of raw data from bridge meas. of Pt100 sensor Public T_Pt_ref 'temp of Pt100 @ ref for TC Units T_Pt_ref=C Public TC_ref 'temp of Reference thermocouple @ ref for TC Units TC_ref=C Public T(16) 'TC temperature at different levels Units T()=C Public I_Fan(17) 'measurement of fan current of up to 16 fans Units I_Fan()=mA 'formatting timestamp according to ETC Dim timestamps_IRGA As String * 22 ' this variable will first receive a timestamp with 22 characters, following this format : yyyy-MM-dd_HH-mm-ss Dim rtime_IRGA(6) As String ' rtime is short for real time Dim timestamps_T As String * 22 ' this variable will first receive a timestamp with 22 characters, following this format : yyyy-MM-dd_HH-mm-ss Dim rtime_T(6) As String ' rtime is short for real time Dim OutStat Dim LastFileName As String *39 'Define Data Tables DataTable (profile-cal,True,1000) 'One record created at each restart of program Sample (1,Q_M,IEEE4) Sample (1,Q_O,IEEE4) CardOut (0,1000)'same size as in logger memory EndTable DataTable (profile-raw,1,-1) Sample (1,Level,FP2) Sample (10,irga(),IEEE4) Sample (1,Q,IEEE4) Sample (1,Flow_meter_ETC,IEEE4) CardOut (0 ,2600000) EndTable DataTable (profile,Store_Trig,10000) Sample (1,Level,FP2) Average (10,irga(),IEEE4,Skip) Average (1,Q,IEEE4,Skip) Average (1,Flow_meter_ETC,IEEE4,Skip) CardOut (0 ,86400) 'auto-allocation would assume one record every second. 'this is unrealistic, 250000 will normally last for >one month EndTable DataTable (ETC_IRGA,1,-1) DataInterval (0,1,Sec,10) CardOut (0 ,260000) TableFile ("CRD:SE-Svb_IRGA_",11,-1,0,1,Day,OutStat,LastFileName) Sample (1,timestamps_IRGA,String) FieldNames ("timestamps") Sample (1,CO2_wet_ETC,IEEE4) FieldNames ("CO2") Sample (1,H2O_wet_ETC,IEEE4) FieldNames ("H2O") Sample (1,Level_ETC,FP2) FieldNames ("LEVEL") Sample (1,T_cell_ETC,IEEE4) FieldNames ("T_CELL") Sample (1,PRESS_cell_ETC,IEEE4) FieldNames ("PRESS_CELL") Sample (1,Flow_meter_ETC,IEEE4) FieldNames("FLOW_VOLRATE") Sample (1,Flow_meter_raw_ETC,IEEE4) FieldNames("FLOW_VOLRATE_IU") EndTable DataTable (ETC_T,1,-1) DataInterval (0,5,Sec,10) CardOut (0 ,52000) TableFile ("CRD:SE-Svb_T_",11,-1,0,1,Day,OutStat,LastFileName) Sample (1,timestamps_T,String) FieldNames ("timestamps") Sample (1,T(1),IEEE4) FieldNames ("TA_2_16_1") Sample (1,T(2),IEEE4) FieldNames ("TA_2_15_1") Sample (1,T(3),IEEE4) FieldNames ("TA_2_14_1") Sample (1,T(4),IEEE4) FieldNames ("TA_2_13_1") Sample (1,T(5),IEEE4) FieldNames ("TA_2_12_1") Sample (1,T(6),IEEE4) FieldNames ("TA_2_11_1") Sample (1,T(7),IEEE4) FieldNames ("TA_2_10_1") Sample (1,T(8),IEEE4) FieldNames ("TA_2_9_1") Sample (1,T(9),IEEE4) FieldNames ("TA_2_8_1") Sample (1,T(10),IEEE4) FieldNames ("TA_2_7_1") Sample (1,T(11),IEEE4) FieldNames ("TA_2_6_1") Sample (1,T(12),IEEE4) FieldNames ("TA_2_5_1") Sample (1,T(13),IEEE4) FieldNames ("TA_2_4_1") Sample (1,T(14),IEEE4) FieldNames ("TA_2_3_1") Sample (1,T(15),IEEE4) FieldNames ("TA_2_2_1") Sample (1,T(16),IEEE4) FieldNames ("TA_2_1_1") EndTable DataTable (T-profile-raw,1,-1) DataInterval (0,1,Min,0) Average (1,T_Pt_ref,FP2,False) Average (1,TC_ref,FP2,False) Average (16,T(),FP2,False) Average (17,I_Fan(),FP2,False)'fan #16 is the fan in the radiation shield for the 'temp/RH probe in the Meteo system, powered from the profile system! 'Background info of logger power status and logger temperature Minimum (1,batt_volt,FP2,0,False) Sample (1,PTemp,FP2)' CardOut (0 ,43200) EndTable DataTable (T-profile,1,-1) DataInterval (0,5,Min,0) Average (1,T_Pt_ref,FP2,False) Average (1,TC_ref,FP2,False) Average (16,T(),FP2,False) Average (17,I_Fan(),FP2,False)'fan #16 is the fan in the radiation shield for the 'temp/RH probe in the Meteo system, powered from the profile system! 'Background info of logger power status and logger temperature Minimum (1,batt_volt,FP2,0,False) Sample (1,PTemp,FP2)' CardOut (0 ,8650) EndTable 'Main Program BeginProg '** System Setup ******************************************************* Scan(5,sec,0,2) ' 'execute twice! Public Q 'mass flow Public Q_raw Dim Q_M Dim Q_O ' Units Q = Nl/Min Units Q_raw = mV Units Q_M = mV Units Q_O = Nl//min Q_M = 0.002 '5000mV=10 Nl/min Q_O = 0 'Offset normally =0, until calibration shows differently 'Public PA 'Public PA_Raw 'Units PA=hPa 'Dim PA_M 'PA_M = 0.12 'Dim PA_O 'PA_O = 500 'Default sequence Skip=true Skip_s=25 '130510/VE 'Skip_s=11 SequenceStep = 30 '30 sec between level switching 130510/VE 'SequenceStep = 15 '15 sec between level switching 'default settigs skip=11 and Sequence Step=15; average of meas from second 12, 13, '14 & 15 will be output! LevelIndex=1 RUNAUTOSEQ = true LevelSequence(1)=1 LevelSequence(2)=2 LevelSequence(3)=3 LevelSequence(4)=4 LevelSequence(5)=5 'Faulty level - blocked or cut tubing LevelSequence(6)=6 LevelSequence(7)=7 LevelSequence(8)=8 LevelSequence(9)=9 LevelSequence(10)=10 LevelSequence(11)=11 LevelSequence(12)=12 LevelSequence(13)=13 LevelSequence(14)=14 LevelSequence(15)=1 LevelSequence(16)=0 ' 0 indicates end of sequence, restart from (1) LevelSequence(17)=0 LevelSequence(18)=0 LevelSequence(19)=0 LevelSequence(20)=0 LevelSequence(21)=0 LevelSequence(22)=0 LevelSequence(23)=0 LevelSequence(24)=0 LevelSequence(25)=0 LevelSequence(26)=0 LevelSequence(27)=0 LevelSequence(28)=0 LevelSequence(29)=0 LevelSequence(30)=0 LevelSequence(31)=0 LevelSequence(32)=0 M_Level_14 = 2 M_Level_13 = 2 M_Level_12 = 2 M_Level_11 = 2 M_Level_10 = 2 M_Level_9 = 2 M_Level_8 = 2 M_Level_7 = 2 M_Level_6 = 2 M_Level_5 = 2 M_Level_4 = 2 M_Level_3 = 2 M_Level_2 = 2 M_Level_1 = 2 M_VentPump = 1 M_SmplPump = 2 NAN_to_full_30min=1 If ToRestart = 0 Then CallTable profile-cal ToRestart = 1 CO2_wet_ETC=NAN H2O_wet_ETC=NAN T_cell_ETC=NAN PRESS_cell_ETC=NAN If LevelSequence(5)=5 Then 'To try and set Level 5 (20m) values to NAN CO2_wet_ETC=NAN H2O_wet_ETC=NAN EndIf NextScan Scan (200,mSec,3,0) LI7200(irga_fast(),1,8,2) AvgRun(irga(),10,irga_fast(),5) CO2_wet_ETC_fast=irga(3)*(8.314*(irga(9)+273.15))/irga(6) H2O_wet_ETC_fast=irga(4)*(8.314*(irga(9)+273.15))/(1000*irga(6)) AvgRun(CO2_wet_ETC,1,CO2_wet_ETC_fast,5) AvgRun(H2O_wet_ETC,1,H2O_wet_ETC_fast,5) T_cell_ETC=irga(9) PRESS_cell_ETC=irga(6) If Level_ETC=10 Then 'To try and set Level 5 (20m) values to NAN? CO2_wet_ETC_fast=NAN H2O_wet_ETC_fast=NAN EndIf If NAN_to_full_30min=1 Then CO2_wet_ETC=NAN H2O_wet_ETC=NAN T_cell_ETC=NAN PRESS_cell_ETC=NAN EndIf NextScan SlowSequence Scan (1,Sec,0,0) 'creating correct format of timestamp for files going to ETC timestamps_IRGA=Status.timestamp(6,0) ' option 6 gives timestamp with format "yyyy-MM-dd_HH-mm-ss.ff" rtime_IRGA(1)=Mid(timestamps_IRGA,1,4) ' yyyy rtime_IRGA(2)=Mid(timestamps_IRGA,6,2) ' mm rtime_IRGA(3)=Mid(timestamps_IRGA,9,2) ' dd rtime_IRGA(4)=Mid(timestamps_IRGA,12,2)' HH rtime_IRGA(5)=Mid(timestamps_IRGA,15,2)' MM rtime_IRGA(6)=Mid(timestamps_IRGA,18,2)' ss timestamps_IRGA=rtime_IRGA(1)+rtime_IRGA(2)+rtime_IRGA(3)+rtime_IRGA(4)+rtime_IRGA(5)+rtime_IRGA(6) VoltDiff(Flow_meter_raw_ETC,1,mV5000,7,1,0,50,1.0,0)) Flow_meter_ETC=0.0025*Flow_meter_raw_ETC-2.5 CallTable ETC_IRGA VoltDiff (Q_raw,1,mV5000,5,True ,0,250,1.0,0) 'Calculate Q Q=Q_raw*Q_M+Q_O 'LI7200(irga(),1,8,2) CallTable (profile-raw) 'collect raw data Store_Trig=false If IfTime (0,SequenceStep,Sec)Then Store_Trig=true LevelIndex=LevelIndex+1 EndIf CallTable (profile) If IfTime (Skip_s,SequenceStep,Sec)Then Skip=false If IfTime (0,SequenceStep,Sec)Then Skip=true If IfTime (0,30,Min) Then LevelIndex = 1 NAN_to_full_30min=0 EndIf If IfTime (0,30,Min) Then LevelIndex = 1 Level=LevelSequence(LevelIndex) If Level=0 Then LevelIndex =1 'restart if eos detected Level=LevelSequence(LevelIndex) If LevelIndex >= 32 Then LevelIndex=32 If RUNAUTOSEQ = false Then Level=0 LevelIndex=1 EndIf For n=1 To 14 If Level =(n)Then a(1,n)=1 Else a(1,n)=0 EndIf Next n If Level=1 Then Level_ETC=14 If Level=2 Then Level_ETC=13 If Level=3 Then Level_ETC=12 If Level=4 Then Level_ETC=11 If Level=5 Then Level_ETC=10 'Level 5 is 20 m which has damaged tube If Level=6 Then Level_ETC=9 If Level=7 Then Level_ETC=8 If Level=8 Then Level_ETC=7 If Level=9 Then Level_ETC=6 If Level=10 Then Level_ETC=5 If Level=11 Then Level_ETC=4 If Level=12 Then Level_ETC=3 If Level=13 Then Level_ETC=2 If Level=14 Then Level_ETC=1 If NAN_to_full_30min=1 Then Level_ETC=NAN 'LevelIndex>7 OR LevelIndex<1 'Always run sample pump if any level is active! a_SmplPump =0 For n=1 To 15 If a(1,n)=1 Then a_SmplPump =1 Next n For n = 1 To 16 If (M(1,n)>= 2) Then o(1,n)= a(1,n) Else o(1,n)= M(1,n) EndIf Next n For n = 1 To 16 If (M(2,n)>= 2) Then o(2,n)= a(2,n) Else o(2,n)= M(2,n) EndIf Next n SDMCD16AC (o(1,1),1,0) SDMCD16AC (o(2,1),1,1) NextScan SlowSequence Scan (5,Sec,0,0) 'creating correct format of timestamp for files going to ETC timestamps_T=Status.timestamp(6,0) ' option 6 gives timestamp with format "yyyy-MM-dd_HH-mm-ss.ff" rtime_T(1)=Mid(timestamps_T,1,4) ' yyyy rtime_T(2)=Mid(timestamps_T,6,2) ' mm rtime_T(3)=Mid(timestamps_T,9,2) ' dd rtime_T(4)=Mid(timestamps_T,12,2)' HH rtime_T(5)=Mid(timestamps_T,15,2)' MM rtime_T(6)=Mid(timestamps_T,18,2)' ss timestamps_T=rtime_T(1)+rtime_T(2)+rtime_T(3)+rtime_T(4)+rtime_T(5)+rtime_T(6) PanelTemp (PTemp,_50Hz) Battery (batt_volt) BrHalf4W (RS_R0,1,mV25,mV25,3,Vx1,1,2035,True ,True ,20000,_50Hz,1.0,0) PRT (T_Pt_ref,1,RS_R0,1.0,0) '20ms settling time proven more than OK for the ref Pt sensor at 'Norunda TCDiff (TC_ref,1,mV2_5C,6,TypeE,T_Pt_ref,True ,0,_50Hz,1.0,0) 'Activate mux PortSet (4,1 ) 'Mux step 1 PortSet (5,1 ) Delay (0,10,mSec) PortSet (5,0 ) 'Mux step one step 'TCDiff (T(3),1,mV2_5C,1,TypeE,TC_ref,True ,0,_50Hz,1.0,0) 'VoltSe (I_Fan(1),1,mV5000,3,0,0,_50Hz,1.0,0) VoltSe (I_Fan(3),1,mV5000,4,0,0,_50Hz,1.0,0) 'Mux step 2 PortSet (5,1 ) Delay (0,10,mSec) PortSet (5,0 ) 'Mux step one step TCDiff (T(3),1,mV2_5C,1,TypeE,TC_ref,True ,0,_50Hz,1.0,0) VoltSe (I_Fan(4),1,mV5000,3,0,0,_50Hz,1.0,0) VoltSe (I_Fan(5),1,mV5000,4,0,0,_50Hz,1.0,0) 'Mux step 3 PortSet (5,1 ) Delay (0,10,mSec) PortSet (5,0 ) 'Mux step one step TCDiff (T(4),1,mV2_5C,1,TypeE,TC_ref,True ,0,_50Hz,1.0,0) VoltSe (I_Fan(6),1,mV5000,3,0,0,_50Hz,1.0,0) VoltSe (I_Fan(7),1,mV5000,4,0,0,_50Hz,1.0,0) 'Mux step 4 PortSet (5,1 ) Delay (0,10,mSec) PortSet (5,0 ) 'Mux step one step TCDiff (T(5),1,mV2_5C,1,TypeE,TC_ref,True ,0,_50Hz,1.0,0) VoltSe (I_Fan(8),1,mV5000,3,0,0,_50Hz,1.0,0) VoltSe (I_Fan(9),1,mV5000,4,0,0,_50Hz,1.0,0) 'Mux step 5 PortSet (5,1 ) Delay (0,10,mSec) PortSet (5,0 ) 'Mux step one step TCDiff (T(6),1,mV2_5C,1,TypeE,TC_ref,True ,0,_50Hz,1.0,0) VoltSe (I_Fan(10),1,mV5000,3,0,0,_50Hz,1.0,0) VoltSe (I_Fan(11),1,mV5000,4,0,0,_50Hz,1.0,0) 'Mux step 6 PortSet (5,1 ) Delay (0,10,mSec) PortSet (5,0 ) 'Mux step one step ' I=I+1 TCDiff (T(7),1,mV2_5C,1,TypeE,TC_ref,True ,0,_50Hz,1.0,0) VoltSe (I_Fan(12),1,mV5000,3,0,0,_50Hz,1.0,0) VoltSe (I_Fan(13),1,mV5000,4,0,0,_50Hz,1.0,0) 'Mux step 7 PortSet (5,1 ) Delay (0,10,mSec) PortSet (5,0 ) 'Mux step one step TCDiff (T(8),1,mV2_5C,1,TypeE,TC_ref,True ,0,_50Hz,1.0,0) VoltSe (I_Fan(14),1,mV5000,3,0,0,_50Hz,1.0,0) VoltSe (I_Fan(15),1,mV5000,4,0,0,_50Hz,1.0,0) 'Mux step 8 PortSet (5,1 ) Delay (0,10,mSec) PortSet (5,0 ) 'Mux step one step TCDiff (T(9),1,mV2_5C,1,TypeE,TC_ref,True ,0,250,1.0,0) VoltSe (I_Fan(16),1,mV5000,3,0,0,_50Hz,1.0,0 VoltSe (I_Fan(17),1,mV5000,4,0,0,_50Hz,1.0,0)) 'Fan 17 in _climate system T/RH probe 'but powered from _profile system 'Mux step 9 PortSet (5,1 ) Delay (0,10,mSec) PortSet (5,0 ) TCDiff (T(10),1,mV2_5C,1,TypeE,TC_ref,True ,0,_50Hz,1.0,0) 'no SE to this channel 'Mux step 10 PortSet (5,1 ) Delay (0,10,mSec) PortSet (5,0 ) TCDiff (T(11),1,mV2_5C,1,TypeE,TC_ref,True ,0,_50Hz,1.0,0) 'no SE to this channel 'Mux step 11 PortSet (5,1 ) Delay (0,10,mSec) PortSet (5,0 ) TCDiff (T(12),1,mV2_5C,1,TypeE,TC_ref,True ,0,_50Hz,1.0,0) 'no SE to this channel 'Mux step 12 PortSet (5,1 ) Delay (0,10,mSec) PortSet (5,0 ) TCDiff (T(13),1,mV2_5C,1,TypeE,TC_ref,True ,0,_50Hz,1.0,0) 'no SE to this channel 'Mux step 13 PortSet (5,1 ) Delay (0,10,mSec) PortSet (5,0 ) TCDiff (T(14),1,mV2_5C,1,TypeE,TC_ref,True ,0,_50Hz,1.0,0) 'no SE to this channel 'Mux step 14 PortSet (5,1 ) Delay (0,10,mSec) PortSet (5,0 ) TCDiff (T(15),1,mV2_5C,1,TypeE,TC_ref,True ,0,_50Hz,1.0,0) TCDiff (T(2),1,mV2_5C,2,TypeE,TC_ref,True ,0,_50Hz,1.0,0) 'no SE to this channel 'Mux step 15 PortSet (5,1 ) Delay (0,10,mSec) PortSet (5,0 ) TCDiff (T(16),1,mV2_5C,1,TypeE,TC_ref,True ,0,_50Hz,1.0,0) 'no SE to this channel 'Mux step 16 PortSet (5,1 ) Delay (0,10,mSec) PortSet (5,0 ) TCDiff (T(1),1,mV2_5C,1,TypeE,TC_ref,True ,0,_50Hz,1.0,0) 'reset mux PortSet (4,0 ) CallTable T-profile '5-min temp data CallTable T-profile-raw '1-min temp data CallTable ETC_T NextScan EndProg
Yes, you can use an If statement to set a value to NAN if not within a range. I suggest writing out all of your logic plainly before writing code to do what you describe.
'Define Data Tables. DataTable (Test,1,-1) 'Set table size to # of records, or -1 to autoallocate. DataInterval (0,1,Sec,10) Sample (1,CO2,IEEE4) EndTable 'Main Program BeginProg Scan (1,Sec,0,0) If (CO2 > 500) OR (CO2 < 10) Then CO2 = NAN EndIf CallTable Test NextScan EndProg
PS. Your program is compiling in sequential mode. You will likely skip scans if not compiling in pipeline mode.
Thank you for the reply JDavis, this is what I though. I'll have a look at the program again. Thanks for the tip about the mode; we do get alot of skipped scans on this program. I will aim to get it into pipeline mode.