There was a change in firmware 5.0 from CR1000X that affected some of our measurements. In the past, we were doing the following:
Const ws_aux = 1.0 Public SE_1 Public SE_2 Public wd DataTable (Main,1,-1) DataInterval (0,10,Min,10) WindVector (1,ws_aux,wd,IEEE4,False,0,0,0) FieldNames ("wd_VecSpd_Avg:,wd_VecDir_Avg:,wd_VecDir_Std:") EndTable BeginProg Scan (1,Sec,0,0) VoltSe (SE_1,1,mV5000,1,True ,0,_50Hz,1.0,0) VoltSe (SE_2,1,mV5000,2,True ,0,_50Hz,1.0,0) wd = (SE_1/SE_2*369) CallTable Main NextScan EndProg
Everything was working fine but when we updated the firmware in our dataloggers, and kept the same programs, we noticed that wd_VecDir_Avg is always zero. After some testing we came out to the conclussion that the issue happens when:
1. Parameter "Speed/East" from WindVector instruction is a constant.
2. Patameter "OutputOpt" from WindVector instruction is 0
In order to solve this problem we had to update the programs in dataloggers with firmware >= 5.0 to change the line:
Const ws_aux = 1.0
To:
Dim ws_aux = 1.0
This solved the problem and now we get correct Vector Mean Wind Direction values.
I tried contacting our sales representative but the conversation got nowhere.
Can anyone from Campbell please tell me why this happens? In the revision history from firmware 5.0 I didn't find anything about this. Can this be fixed in a newer version so WindVector produces Vector Mean Wind Direction values that are correct and not zero? Some colleagues have reused old programs (Const ws_aux = 1.0) in dataloggers with latest firmware (6.0) and we still have the same problem.